THEORY OF OPERATION OF WATTHOUR METERS
Basically, the watthour meter consists of a motor whose torque is proportional to the power flowing through it, a magnetic brake to retard the speed of the motor in such a way that it is proportional to power, and a register to count the numbers of revolutions the motor makes.
There are three principle torques involved in the operation of a watthour meter; first, the propelling torque of the motor element; second, the retarding torque of the magnetic brake; and third, the retarding torque due to friction.
The motor is made up of a stator and a disk. The stator has two windings. One of them, the Current Coil, is connected in series with the load and the other, the Potential Coil, is connected across the line and carries a current proportional to the voltage of the circuit. The split phase effect causing rotation is developed by winding the current coil with few turns and by winding the potential coil with many turns of fine wire making its magnetic circuit of low reluctance and high reactance. As a result, the current in the potential coil is made to lag almost 90? behind the line voltage. The potential coil with its core is commonly referred to as the Voltage Electromagnet and the current coil with its core as the Current Electromagnet.
The magnetic flux set up by the voltage electromagnet extends across the air gap over to the iron core of the current electromagnet. Similarly, the magnetic flux set up by the current electromagnet extends across the air gap over to the iron core of the voltage electromagnet. The resultant flux of the voltage and current electromagnets then passes through the disk of the meter, and since there is a difference in phase between the two separate fluxes, the resultant flux undergoes a continual shift or ?sweep? from one side to the other, always in the same direction. The eddy currents set up in the disk as a result of the magnetic flux penetration, react with this shifting flux pattern and cause the disk to rotate.
The torque on the disk caused by the interaction of fluxes tends to cause constant acceleration. Without a brake the speed of rotation would be limited by the supply frequency, by friction, and by certain counter torques at higher speeds but the speed of rotation would be very high. Therefore, some method of making the speed proportional to power and also of reducing it to a usable value is needed. A permanent magnet performs these functions. When the disk is rotated in the field of the permanent magnets the eddy currents set up in the disk react with the magnetic flux from the permanent magnets in such a manner that there is a retarding torque or ?drag? applied to the disk which is always directly proportional to the speed. For this reason, the permanent magnets are referred to as ?Drag Magnets?.
METER ERROR SOURCES
1) TEMPERATURE ERROR
Meters read high between 0 and 88F and low thereafter. Error accentuates with decreasing PF and alone can be as high as 4% at 0.5 PF. The main caused of this error is the increase in the voltage coil lag at low temperatures (temporary error) and demagnetization of the braking magnets permanent error at high temperatures. ALL PERMANENT MAGNETS DEMAGNETIZE WITH TIME, THE RATE OF WHICH IS DETERMINED BY EMPERATURE, TIME, QUALITY, AND ELECTROMAGNETIC FIELD EXPOSURE. The demagnetization of braking magnets ALWAYS results in rotor speed-up and over registration!
2) FREQUENCY ERROR
frequency seldomly varies more than ~ 1% from 60 or 50 Hz. a 10% variation of line frequency can result in a 1% or more error, particularly for high PFs. Meter reads high at low frequencies to a point and low at high frequencies. Meter can perform erratically when harmonically rich waveforms (eg rectified sine wave) is applied to it at appreciable energy levels. Error is higher for low PF loads at low frequency.
3) VOLTAGE ERROR
Generally, line voltage is stable to within+10% of rated. In cases of over voltage, watthour meters read substantially low due to significant AC damping that results in some braking. This phenomenon is called "overload droop" and is slightly higher for low PF. Watthour meters read slightly high when voltage is low.
This statement is invalid. The average of a periodic function is defined as its integral over its period. When you take an average, you have to define the function and its period, otherwise its a meaningless number.NotLurking said:However I did state that the average is 63.6% of maximum value.
Your first point in this paragraph:NotLurking said:Item #2 - I?m familiar with Maxwell (and his law), Weber, Gauss, Tesla.and also Michael Faraday. In an AC power circuit there in no DC current. In fact, if a DC component is present in a transformer ...
.[/B]
By definition, circuits that are comprised of inductors and capacitors only do not consume power!! In these circuits, energy just keeps getting transferred from magnetic to electric.NotLurking said:Item #4 ? OTOH, if we are considering AC circuits that have inductance or capacitance reactance then current consumption will increase as voltage decreases.
.[/B]